JAZZ 20 Modbus RS485 connection to Unicloud
Ori Ziv
Oct-28th, 2024 10:12
Configuration Modbus -RS485 Parameters for Jazz unit – and connect to Unicloud with Modbus Slave connection type.
Use the example project I sent you and this is the explanation on every step of configuring the serial communication to RS485
Parameter
Store into SI
Function
Network ID
141
Range: 0-255.
This is the Network ID number of the device on the network. You can either assign an ID via an MI, or directly via a constant number. Do not assign the same ID number to more than one device
Time out
142
Time out units:10 msecs; a Time out value of 100 is equal to 1 second.
This is the amount of time a master device will wait for an answer from a slave.
Retries
143
This is the number of times a device will try to send a message.
Maximum Time Delay
144
Time units: 2.5 msec.
This is the maximum time interval permitted between 2 messages. This should be set to 2, setting the permitted interval to 5 msecs (n x 2.5 =interval).
Baud Rate
145
Store the value into SI 145 to set the baud rate.
Note that Jazz does not support the following baud rates: 110, 38400, 57600. In addition, ‘2’ Stop Bits is not supported. In Jazz controllers; use Function 310 to modify the default settings of an Add-on Port.
Legal Baud rates are:
110
300
600
1200
2400
4800
9600
19200
38400 (store 384)
57600 (store 57600)
Call MODBUS Configuration
140
This must be the final parameter stored.
Storing the value 600 into SI 140 configures the controller for MODBUS.
Storing the value 599 into SI 140 configures the controller for MODBUS and also enables Unitronics' PC applications to access the PLC.
After the parameters below have been stored into the appropriate SIs, initialize the COM port by storing 310 into SI 140.
SB 141 indicates whether the COM port has been successfully initialized with the new parameters successfully: 1 = success, 0 =fail.
Parameter
Store to SI
M91
Jazz: MJ20-RS
Jazz: MJ20-PRG
Baud Rate
141
Legal Baud rates
Store value into SI 141 to set baud rate.
  • 110
  • 300
  • 600
  • 1200
  • 2400
  • 4800
  • 9600
  • 19200
  • 38400 (store 384)
  • 57600 (store 576)
  • 300
  • 600
  • 1200
  • 2400
  • 4800
  • 9600
  • 19200
  • 300
  • 600
  • 1200
  • 2400
  • 4800
  • 9600
Data bits
142
  • 7
    8
Parity
143
  • 0=even
    1=odd
    2=none
Hardware Flow Control
144
  • 0=No Flow Control
  • 1=Flow Control
RS232:
  • 0=No Flow Control
  • 1=Flow Control
  • 2=enable RS485 and RS232
Note that in order to implement RS485, you must write 2 to SI144
Always write 0
Time out
145
Time out units:
  • secs; a Time out value of 100 is equal to 1 second. Legal values:
    50
    100
    150
    200
    500
    6000
Stop bits
146
  • 1
  • 2
2 stop bits is not supported
COM Init
140
Storing the value 310 into SI 140 initializes the COM port with the new parameters.
Second setting
Wiring procedure:
RS485 Connector Pinout
  • Pin 1: D_N (Driver negative signal)
  • Pin 2: R_N (Receiver negative signal)
  • Pin 3: GND (Device ground)
  • Pin 4: D_P (Driver positive signal)
  • Pin 5: R_P (Receiver positive signal)
  • Pin 6: NC (Not connected
Router parameters
Modbus commends to check connectivity first using the modbus serial master.
UniCloud
After you manage to made the connection with RS485 and read MI 10 for example, you need to connect device to Unicloud by “Modbus slave” connection type just follow the help files in Unicloud website/your organization.
Just follow the Unicloud section one by one and fill every thing like the guide tells you.
Mind that you are required to create Modbus slave serial number that will pop up like on the picture below:
Unicloud Help files for Modbus link:
https://unitronics.cloud/unicloud_help/#t=MODBUS.htm
3 out of 5 found this helpful